Reinforcement

Tolerance on Placing of Reinforcement

Tolerance on Placing of Reinforcement

Unless otherwise specified by the Engineer-in-charge, reinforcement shall be placed within the following tolerances:

Tolerance in spacing

a) For effective depth, 200 mm or less + 10 mm

b) For effective depth, more than 200 mm + 15 mm

Cover to Reinforcement :

The cover shall in no case be reduced by more than one third of specified cover or 5mm  whichever  is  less.  Unless  indicated  otherwise  on  the  drawings,  clear  concrete  cover  for reinforcement (exclusive of plaster or other decorative finish shall be as follows) :a) At each end of reinforcing bar not less than 25 mm, nor less than twice the diameter of such bar.

a) At each end of reinforcing bar not less than 25 mm, nor less than twice the diameter of such bar.

b) For a longitudinal reinforcing bar not less than 25 mm, nor more than 40 mm, nor less than the diameter of such bar. In the case of column of maximum dimensions of 200mm or under, whose reinforcing bars do not exceed 12mm, a cover of 25mm may be used.

c) For longitudinal reinforcing bar in a bar, not less than 25 mm nor less than the diameter of such bar and.

d) For tensile, compressive, shear, or other reinforcement in a slab, not less than 25mm,nor less than the diameter of such bar and.

e) For any other reinforcement not less than 15mm, nor less than the diameter of such bar.

f) Increased cover thickness may be provided when surfaces of concrete members are exposed to the action of  harmful  chemicals  (as  in  the  case  of  concrete  in  contact  with  earth  faces contaminated with such chemicals), acid, vapour, saline, railways) etc. and such increase of cover may be between 15mm and 50 mm beyond the figures given in (a to e) above as may be specified by the Engineer-in-charge.

g) For reinforced concrete members, totally immersed in sea water the cover shall be 40mm, more than specified ( a to e) above.

h) For reinforced concrete members, periodically immersed in sea water or subject to sea spray, the cover of concrete shall be 50 mm more than that specified (a to e) above.

i) For concrete of grade M25 and above, the additional thickness of cover specified in (f),(g) and (h)  above  a  my  be  reduced  to    In  all  such  cases  the  cover  should  not exceed 75mm.

j) Protection to reinforcement in case of concrete exposed to harmful surroundings may also be given by providing a dense impermeable concrete with approved protective coating as specified on the drawings. In such case, the extra cover, mentioned in (h) and (i) above, may be reduced by the Engineer-in-charge, to those shown on the drawing.

k) The correct cover shall be maintained by cement mortar briquettes or other approved means. Reinforcement for footings, grade beams ad slabs  on  sub  grade shall  be  supported  on  precise concrete  blocks as  approved by the Engineer-in-charge.  The use of pebbles  or stones  shall  be permitted.

l) The minimum clear distance between reinforcing bars shall be in accordance with IS 456 or as shown in drawings.

Related Articles

Leave a Reply

Your email address will not be published. Required fields are marked *

Back to top button
Follow Engineers

Civil Engineering Job Update in WhatsApp

click on the below link to join
Join Now
close-link
World’s Biggest Cruise Ship Construction Work Checklist Autocad 2d Plan with 3d Elevation